Industrial electricity
the electric saw is activated when the braker is operated
pablo rocha
The electric saw has a control system with a contactor and a thermal relay and when I climb the breaker it turns on alone without pressing the button and when I try to turn off with the off button the contactor jumps a little but does not turn off, but if it turns off by pressing the button that has the relay but as it is a button it is obviously on.
JulioCesarTorres
The logic says that the contactor coil is receiving current, measure this point with voltmeter.
pablo rocha
mmmm if it is receiving current without activating the ignition button .. that is the problem
chispa41
chispa41
209
You should discriminate the control circuit and the power circuit, that is: I would disconnect the coil from the contactor (A1 and A2) and check if it continues to activate. If so, the problem is in the contactor, but in the control circuit.
pablo rocha
ah ok perfect, I will see what happens.
Hi. Do you have a stop / run circuit? Check the buttons. The start must be normal open (NA) and the normal stop closed (NC) Begin by checking these buttons to rule out problems. Cheers
pablo rocha
I already checked the continuity and everything and both are well and remains the same.