Industrial electricity
Three-phase 380 V phases
fede21
fede21
2
hace 6 años
hace 6 años
Hi. I have to connect 2 resistors (4 terminals) in star with three-phase 380, a single phase can feed 2 resistors. I connected them in a triangle and a resistance broke out. How do I connect in a star? Can I use a single phase of 3? Thank you ..
neybero
neybero
46
hace 6 años
You must first make sure that the voltage of the resistors is 380 volts. Then you connect the resistors in series. You will have two terminals at the ends and one at the central point or junction of the resistors. Each of these points corresponds to a phase.
elektomaq
elektomaq
62.202
hace 6 años
elektomaq
elektomaq
62.202
hace 6 años
hace 6 años
Hello To connect in star or triangle, you need at least three resistors, you cannot do it with 2 In turn, each resistance must be 220 if you connect it in a star or 380 if you connect it in a triangle If the resistance was for 220 and you connected it in a triangle at 380 it is obvious that you are going to burn it If the resistance is 220 you can connect them between phase and neutral. You can use a phase for each one and the neutral as common but the ideal would be to recover the burnt resistance because the fault will be noticed, it will not get to heat what it has to heat Regards
neybero
neybero
46
hace 6 años
Make the connection that I explained to you that neither resistance will be burned. But confirm that they are at line voltage. This connection is called open Delta.