Household Electricity
replace tertapolar circuit breaker with three bipolar
pibenesto
hace 6 años
hace 6 años
Hello dear foristas, I had a problem with a 40A tetrapolar circuit breaker that practically melted in two of its inputs in the neutral and one phase, a consumption of 30A or so is applied to a 4x6mm sintenax cable. What would be better? Replace said circuit breaker with another one of better quality. The melt is SICA or place 3 bipolar circuit breakers and thus balance the loads on each one of them? Thank you
hace 6 años
hace 6 años
Hi. If there are three-phase loads if or if you must replace it with another one. If there are not, you can place three bipolar without problems. Adjust the terminals of the new differential well so there will be no overheating problems like the one that failed. Regards
elektomaq
elektomaq
62.202
hace 6 años
I agree
nastor
nastor
17.232
hace 6 años
hace 6 años
Hi Pibe If you refer to the main circuit breaker differential, the answer is no; promptly in that case you cannot replace them with three bipolars since the regulation requires ONE differential circuit breaker. If it is in sectional boards, there is no problem as you connect a power cutter (since it will be one after the existing one), this in the case of having only single-phase circuits.