Household Electricity
Home electrical network
Damian22
hace 6 años
hace 6 años
Good ... I have doubts about my electrical installation. .. I was watching and reading a bit and I think it's wrong ... I have from the meter to the entrance of the cable house 2 x 4mm symptoms that enters the dilemma of 25 A ... from a and a bridge with the same cable comes to a thermal of 25A ... of the therma leaves a single circuit with 2.5mm cable the house is small has 2 rooms a kitchen dining room girl and bathroom ... we have 3 outlets in the kitchen to dining room. ..2 shots in each piece and in the bathroom an electric thermometer. .. I have a frost, 2 TVs and 6 light bulbs ... sometimes I use electric kettle ... and now with the cold 1 calloventor and an electric stove that go simultaneously ... and I see that the thermal Warms up a little enough for my taste .... Sometimes when there is low voltage ý I have the stoves on and plug the electric boiler jumps the thermal ... unplugs a stove and walks normal ...
elektomaq
elektomaq
62.202
hace 6 años
hace 6 años
Hello Damian I'm going to recommend a couple of things 1) Edenor 63A thermal is incorrect, but it is not your competence, if Edenor really put it, let them take care ... 2) the sintenax cable of 4 mm2 is recommended to replace it with a 6 mm2 cable 3) the heat of 25 I recommend it be 32 4) the differential I recommend be 40 5) make the circuits divided as indicated by Servimat1 A) Water heater (conductor 2.50mm2, thermal 16A) B) Outlets (conductor 2.50mm2, thermal 16A) C) lighting (conductor 1.50mm2, thermal 10A) second option : A) kitchen (driver 2.50mm2, thermal 16A) B) bathroom (driver 2.50mm2, thermal 16A) C) rest of the house (conductor 2.50mm2, thermal 16A) Do not forget the grounding regards
hace 6 años
Excellent.
hace 6 años
hace 6 años
Hi. Actually for what you comment you have only one electrical circuit in the house. They should be two or three as for shots, lighting and socket of the electric boiler. This way you could already distribute the charges in the different circuits. Note that the sum of all charges possibly exceeds the nominal capacity of the cable. You should not under any circumstances increase the capacity value of the thermal so that it does not heat up or jump since you could start a fire. The thermal of the meter what value is it? regards
Damian22
hace 6 años
The thermometer of the meter placed by edenor is of 63A ... from a and it leaves the cable of 4mm for the circuit breaker of 25A, the bridge of the thermal circuit breaker 25A is of 4mm ... and of the output of the thermal 25A leaves cable of 2.5 mm for the whole house ... it's fine like that. ? My question is ... the 2.5 cable is fine for the thermal 25A ... what if I'm sure that I should not change the heat for nothing because if I do this I must change all the cables ... I also know that the thermal it must be equal or less protected than the circuit breaker ...
Damian22
hace 6 años
Thanks x answer ...
hace 6 años
The thermal for the 2.5 mm² cable should be 16 amperes and 20 amperes if the cables meet modern standards. The issue is that with that cable you can handle not all the cargo. To do something safe you have to change the general cable and place a board with more circuits inside the house. Although the physical size of the house is small, all you have is electricity.
Damian22
hace 6 años
Ok ... thanks I was thinking about doing that separate x circuit ... I mean that what I have done is wrong ... X at least I know that the thermal works by overloading jump xq and that's good no, otherwise I would have a fire
hace 6 años
Follow the advice of the friend elektomaq for a good electrical distribution and you will not have problems.