Good afternoon, I would like you to orient me a bit with my electrical installation project. I am in the construction stage of my house with two floors and I want to make a line for [b] lights of 1.5mm, another for sockets of 2.5mm and another for 4mm radiant air / floor. I want to show you the drawing I made: And I would also like to know if the connection of a point and socket is okay like this: I would like to know if it is well posed. I await comments. regards
elektomaq
elektomaq
62.202
hace 6 años
Hello
One doubt ... how many kw / hour does the underfloor heating consume?
Andrés713
hace 6 años
hace 6 años
Hi, if you want to separate the lighting circuits and outlets, in the second image you would lack a neutral of lighting, because you are using the neutral of the outlets
andresf
hace 6 años
Ah, ready. Thank you
agustinp
agustinp
2.247
hace 6 años
hace 6 años
It is not quite the connection ... first of all you would have to put a minimum pipe 1 "to pass such a number of cables, other you lack a neutral that by deduction, I see that is missing because you did unipolar cut on the board only of the phases, and you used a common neutral, which is expressly forbidden That must be corrected
andresf
hace 6 años
Thanks Agustín. I still have not wired, so I consulted. Now I have to check if that number of wires come in. Thank you again
agustinp
agustinp
2.247
hace 6 años
Andres, beyond that you have to use only 35% of the internal millimeter section of the pipe. It is not so much to pass comfortable cables if not to leave ventilation
agustinp
agustinp
2.247
hace 6 años
for one of 7/8 you can not pass more than two circuits ... therefore it would be convenient in any case to make square pass boxes from the feed and go down in each environment ... or the other would be to pass the cable of 4mm2 by a separate pipe and that does not pass through that total box is not necessary if the circulation is not very long. Evaluate yourselves. regards
andresf